riello burner

eyeball
eyeball Member Posts: 3
i have a riello mec 3ka burner looking for service booklet went to riello website couldn't find anything . unit was running fine until it was switched to powervent from old chimney.burner producing to much smoke .any help would be greatly appreciated.

Comments

  • Robert O'Brien
    Robert O'Brien Member Posts: 3,562
    That burner

    was discontinued over 25 years ago,time for an upgrade! You aren't trying to use your  eyeball to adjust this are you,Eyeball?
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • heatboy
    heatboy Member Posts: 1,468
    If I had to make a guess.....

    ....I would say the venter is the issue.  Riello burners work their best when firing into a positive pressure chamber area.  The venter may be causing an excessive draft.  What boiler is the burner attached to?  Lining the chimney is, by far, the better option if it can be done.

    There was an error rendering this rich post.

  • eyeball
    eyeball Member Posts: 3
    riello burner

    burner is on a burnham boiler chimney had to come down
  • Steamhead
    Steamhead Member Posts: 17,344
    edited March 2010
    Heatboy is on to something

    check the draft. Too much draft will pull the flame right off the burner head (we call it "loss of retention") and cause a smoky fire.



    Is there a draft regulator between the boiler and the power venter? What size is it? What size is the breech (flue outlet) on the boiler? What is the draft at the breech? What model Burnham is it?



    BTW, according to Firedragon, there are only detail differences between the Riello MEC and 40-series burners. I don't have his books in front of me to get the specifics though.....
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Paul Fredricks_3
    Paul Fredricks_3 Member Posts: 1,557
    Nope

    There is a big difference between those 2 burners. A complete remake of the burner. The Mectron which came out after the MEC is similar to the 40 series.
  • Matthew Grallert
    Matthew Grallert Member Posts: 109
    edited March 2010
    That Old MEC

    Didn't they stop with the MEC in 1972 or so.  I've not seen another burner run as long or as well for anywhere near that long.  Great burner, that said it's time I think to replace that old jenny.  It doesn't owe anyone anything:-)

    Peace

    Matthew

    Now I wonder If I have a copy of the manual for one of those.  I'll check tonight.

    If I do I'll copy it for you.
  • toilburn
    toilburn Member Posts: 44
    toilburn

    Yes the burner should be replaced, but I know of at least 15 still running fine.