I thought you would like to hear this.
Two Pipe Bang is fixed :-)
The fix was not to raise the equalizer pipe running to the false water line but the removal of the equalizer to the false water line and the installation of a vapor-stat
As it turns out this is a vapor system it seems to be a cross between a Arco Model K and a Hoffman system.
The only trouble now is the system seems to short cycle but the burner is down fired as low as I can go so I will have to live with that for now.
Thanks Again for your help on this. Rich
2-pipe bang silenced
in regard to short-cycling, are you letting the air out as quickly as possible? inadequate venting is the primary cause of short-cycling at low pressures, unless your boiler is over-sized.--nbc0 -
Yes
This customer had her a/c contractor replace the boiler about 10 years ago there were a number of problems with this install incorrect near boiler piping the lowering of the water line and so on.
My guess is the boiler is one maybe two sections to large and I am sure 2 Gorton 2's would be a better setup than a #75 Hoffman .
But my company just comped about a Grand of piping work to this job thats enough for now.
There is just some things this owner is forced to live with unless they are willing to invest a lot more money. Very unfortunate this should have been done correctly Ten Years Ago.
Thanks For Your Input Rich0
- 87K THE MAIN WALL
- 114 Chimneys & Flues
- 106 Geothermal
- 982 Plumbing
- 388 Solar