Please help identify this Weil-McLain boiler
JohnNY
JohnNY Member Posts: 3,341
Here is the CP number: 2079378
WM can i.d. the date of manufacture but not the model due to a computer issue of some kind. I'd appreciate any help in identifying the model and BTU input/output.
Thanks a bunch.
JohnNY
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
  • Al Letellier_21
    Al Letellier_21 Member Posts: 400
    weil mclain boiler
    Looks like a LGB gas commercial boiler. Looks like it has flame guardian control system that can be L-H-L operated using temperature controls. They were from 6-23 sections in size. Need to know # of sections to determine BTU rating...smallest 6 section is 458MBH or 1646 sq. ft. steam
                            7 section is 549
                            8 section is 641
    add approx 92,000 per section.
  • JohnNY
    Wow. Thanks, Al.
    I can't get access easily to the boiler again, so would counting the burners help determine the number of sections?
    Classes
  • Al Letellier_21
    aclheatdoctor@myfairpoint.net
    Not really as there is no information in the book as to how many tubes per section. Section count is the best, or length of the boiler left to right would do it as well. I counted 15 or 16 tubes in your photo. I will dig a little deeper, Have an installation manual as well and will check that.
  • Al Letellier_21
    number of tubes
    All I can find is that with a single manifold and base, the largest that boiler can be is a 12 section, rated at 1.007MBH or 3,621 sq feet of steam........that's really cooking !!!!  Let me know if you can get some dimensions or section count. Sent you an e-mail. Write back direct if you wish.
    AL