Red Ace Boiler
Dan_43
Member Posts: 58
I have a 6 room apartment with, what I believe is, an old coal converted to oil fired boiler (1 pipe steam system). Its still running fine but the bottom is showing lots of rust and I want to be more proactive then reactive (see picture) I have measured the (6) radiators I have included a picture of the type. the one in the picture is a 2x12 if I read the cart correctly that radiator has 26sq-ft of volume. I have added up square footage of all the radiators and come up with a total of 153 sqft x1.5= 229.5
230sqft x 240= 55,200 BTU
Have I done my math correctly? This seems like a pretty small boiler, then again its only a (6)rm first floor apartment.
thanks in advance for any input.
Dan Z
Dan Z
what chart?
what chart did you use to determine the EDR of the rad? i'm not saying you are incorrect, i'm just wondering your source. thx.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
Crane Radiator
That loooks like a Crane "Standard" Return Bend Wrought Iron Tube Radiator. It's in Dans EDR book page 14, for the radiator in the pick it has a heating surface in square ft. of 240
