Where do you install your boiler fill valves?
I am trying to learn where your boiler fill valve is generally installed on the system? Thank you for your input
  • CMadatMe
    CMadatMe Member Posts: 3,086
    At the Point
    Of no pressure change. If you want to learn Dan has a nice book called "Pumping Away" that you can purchase right here on his site.
  • David Sutton_6
    David Sutton_6 Member Posts: 1,079
    Fill valves
    The best place to locate your fill valve is between your extrol tank and your tie in point just put in a 1/2 tee and add your fill there, its known as the point of no presure change, see the picture below look at the tank and right above it is the point,
    David
  • cwilliams2000
    cwilliams2000 Member Posts: 140
    thank you
    thank you, that pic is great, I think I will end up doing exactly the same thing and be done with the issue. Two side notes, I like Dr Pepper too! :)
    Also why does it look like I dont see the drain flow line coming out of the backflow preventer?
  • R Mannino
    R Mannino Member Posts: 440
    I See
    the Dr. Pepper, but I can't see the Maxwell House. I'm a Smithwick's guy, it's OK I was in the garage at home.
    Ron
  • Devan
    Devan Member Posts: 135
    where if
    you are using a low loss header?
  • David Sutton_6
    The jobs not done yet
  • Ron Jr._3
    Ron Jr._3 Member Posts: 605
    We normally
    pipe the feed into boiler return pipe . You can purge the zones with hot water and know they're all done easier . And if you're closing the PRV down after purging ( with a LWCO ) , the placement of the valve is not critical .