Split Steam System For Church
I will be replacing a 550,000 btu steam boiler with a split 6" supply.
One side supplies 1430 sf of steam to the second floor while the other
side supplies 760 sf of steam to the first floor. It is a one pipe
system but the returns are connected within the walls.
My thoughts are to install thermostat controlled steam valves on each
side to separate (and zone) the two floors. If I cut in a drip legs on
the radiator side of the steam valves and tie them into the return,
will that keep the system from banging?
Any advice for this type of installation will be greatly appreciated.
    Jamie Hall Member Posts: 26,766
    Should work --
    after all, it is sort of like using king size TRVs.
    However, a couple of thoughts.
    First, those drips by the valves are absolutely critical.  Can't get by without them.  Just make sure that you have adequate A dimension, though, up to the steam main, as otherwise there is a real risk of the wet return water pushing back up into the main.
    Second, resist the temptation to use reduced port or globe valves.  You are dealing with saturated steam, which does not take kindly to any short restriction in flow.  You must use full port ball or plug valves in this type of application -- this observation is based both on theory and on field observation.
  • SuburbanHVAC
    SuburbanHVAC Member Posts: 3
    Split Steam System
    Thanks Jamie, any idea who carries a full port motorized steam valve?
    Good grief
    it's been some time since I've gone looking for big motorized valves... no, honestly, I really don't know who makes them -- or carries them.  I do know they exist, though!  I know Hammond makes flanged gate valves in larger sizes (and a gate valve will work), but I don't know about actuators... Honeywell makes an incredible range of valves, and actuators.  I'd probably contact a Honeywell dealer and see what he could do for me.
  • SuburbanHVAC
    Still Looking
    I've had no luck so far, but I'll keep looking. Thanks.
  • MikeyB
    MikeyB Member Posts: 696
    edited January 2010
    Electric Ball Valves
    Hey Surburban, check out Graingers website, I came across DynaQuip Control valves, steam rated, full port, 24v, 120v, might be what you are looking for. You can also check out Dwyer Instruments,Inc
