Help with BTU size and age
JLM
Member Posts: 1
I have an American Standard stem/hot water boiler and I am tyring to find out the BTU rating and age of this unit as I am going to have to replace it very soon. On the front plate it says Square heat type r boiler, net rating 405 MBh, max firing rate 675 MBh and size 3R4M. I know that the BTU rating net would be 405,000 BTU. Should I be looking for a new unit of this size or larger since the max rating is 675,000 BTU?
Some advice,
Get a pro in there to calculate a H/L for the way your house is today.
Believe-me,,, you`ll get away with something much smaller!0 -
As Dave Has Said
Don't worry about the size of this boiler. Have a heat loss done.There was an error rendering this rich post.
Sizing Boiler
Your post says stem/hot water. I presume you mean steam. If steam a boiler is sized by the total EDR of the radiators. If hot water, then you'll need a heat loss calculation to properly size the boiler.0
- 87K THE MAIN WALL
- 113 Chimneys & Flues
- 106 Geothermal
- 981 Plumbing
- 388 Solar