steam coils - F&T trap or thermostatic radiator trap?
Options
Steve_210
Member Posts: 661
Typically on steam coils is it best to use a F&T trap or a thermostatic radiator trap. Each coil is about 10,000 BTU's each.
0
Comments
-
I'd use an F&T
since it will drain condensate more quickly. If the coil sees outside air, I'd include a vacuum breaker so water won't be held up in the coil and possibly freeze.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0