steam coils - F&T trap or thermostatic radiator trap?

Options
Typically on steam coils is it best to use a F&T trap or a thermostatic radiator trap. Each coil is about 10,000 BTU's each.

Comments

  • Steamhead
    Steamhead Member Posts: 16,856
    Options
    I'd use an F&T

    since it will drain condensate more quickly. If the coil sees outside air, I'd include a vacuum breaker so water won't be held up in the coil and possibly freeze. 
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting