Pellet stove for garage workshop?
Jason_44
Member Posts: 60
I want to heat my attached 1-car garage (near Boston) with a pellet stove. I do quite a bit of woodworking in there in the winter.
Are there any code restrictions on having one in a garage? Any Boston-area installers you can recommend?
Jason
Jason
Not allowed in a garage
Not an approved installation.
NFPA 211, (National Fire Protection Association) Standards for Chimneys, Fireplaces, Vents, and Solid Fuel-Burning Appliances states:
"Solid fuel-burning appliances shall not be installed in any garage"
Ed Carey0 -
Are there any exceptions?
Are there any exceptions in the code? I never park cars in there. I use it as a small woodworking shop and do some home fix-up projects in there.
Jason0 -
None that I am aware of
Jason,
The information in quotation was verbatim from the NFPA 211.
NFPA 211 is a Standard, not a Code. However it is unquestionably accepted as a "Standard of Care" in the industry, and it may be codified in many areas.
The only way you could obtain a variance from any NFPA publication would be to get it directly from NFPA, IN WRITING.
If you find a stove that, (in writing) is "Listed and approved for installations in garages" you may be able to present that information to NFPA, and they could potentially recognize that specific equipment manufacturer's "listing" as an exception. However, that would be up to NFPA alone to make such a decision.
A caution, information from an installer such as: "I've been doing this for a gazillion years and have installed many in garages with no problems" is NOT an acceptable exception to the NFPA 211 Standard.
Ed Carey
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam
