EDR for Convector & Sunray steam radiators?
SteamHeat
SteamHeat Member Posts: 159
I have attached a picture of my Convector steam radiator and a picture of my Sunray steam radiator. I wish to calculate the EDR for each. Could someone tell me how?
Thanks in advance for any help.
  • Steve_210
    Steve_210 Member Posts: 664
    governale
    the sunrad is 540 btu,s per section @ 215 degrees F
    we need the size of the convector or you can look on their website
    [url=http://www.governaleindustries.com]www.governaleindustries.com
  • SteamHeat
    The convector is dimensioned as follows:
    3 Sections totaling 30 inches across in width,
    5.5 inches deep madeup of 3 tubes,
    6 inches in height (not including the rods that elevate) comprised of 3 rows,
    if the elevating rods are included, the height is 15 inches off the floor.
    The Sunrad recessed is 18 inches wide comprised of 8 sections (7 openings),
    3.25 inches deep (that I can measure from the front) with visibly 4 slots per opening,
    overall height is 20 inches tall.
    Thank you for your help.
  • Steve_210
    governale
    the closest i can get on the convector is 31 long 6.5 deep installed at 20 high. = 24 edr  24high=26edr        the sunrad  should be 5 deep if so it is 18edr
  • SteamHeat
    EDR for Convector & Sunray radiators?
    Thank you very much for this info. It helps alot.
    Regards.