EDR for Convector & Sunray steam radiators?
SteamHeat
Member Posts: 159
I have attached a picture of my Convector steam radiator and a picture of my Sunray steam radiator. I wish to calculate the EDR for each. Could someone tell me how?
Thanks in advance for any help.
Thanks in advance for any help.
0
Comments
-
governale
the sunrad is 540 btu,s per section @ 215 degrees F
we need the size of the convector or you can look on their website
[url=http://www.governaleindustries.com]www.governaleindustries.com0 -
EDR for Convector & Sunray steam radiators?
The convector is dimensioned as follows:
3 Sections totaling 30 inches across in width,
5.5 inches deep madeup of 3 tubes,
6 inches in height (not including the rods that elevate) comprised of 3 rows,
if the elevating rods are included, the height is 15 inches off the floor.
The Sunrad recessed is 18 inches wide comprised of 8 sections (7 openings),
3.25 inches deep (that I can measure from the front) with visibly 4 slots per opening,
overall height is 20 inches tall.
Thank you for your help.
0 -
governale
the closest i can get on the convector is 31 long 6.5 deep installed at 20 high. = 24 edr 24high=26edr the sunrad should be 5 deep if so it is 18edr0 -
EDR for Convector & Sunray radiators?
Thank you very much for this info. It helps alot.
Regards.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements