wiring H.W. L8148E w/ Taco zone valves
Options
S.A.
Member Posts: 2
I need to wire two taco zone valves with a Honeywell L8148E. The only diag. I can get is w/ H.W. zone valves. I have terminals marked t,tv,w,z the w,z have a jumper needed for 24v sys. I could use an external transformer , but this has become a challenge I really want to know how to wire it this way. But I don't want to toast the control, $$$.
0
Comments
-
Go from the "Z" terminal
on the relay to the thermostat then out of the thermostat to terminal # 1 on the Taco ZV. Then "TV" goes to # 2 terminal on the ZV and finally "T" goes to # 3. You should be all set.0