compressor replacement
ddenny
Member Posts: 75
I have a trane rooftop a/c unit with a grounded 3 phase scroll compressor. the suction and discharge lines are brazed on; those unique conections you see on a lot of tranes are not used on this one.
trane told me it was a 4.8 ton compresor. can I replace it with a 5 ton copeland scroll? is a 4.8 the same as or close enough to a 5 ton copeland. I forgot the manufacturer's name (of the grounded compressor). thank you
Hi Dennis
You're be fine.The only issue I might see is being able to mount the scroll to the base of the unit.0 -
Denis, I agree
Those fittings you are talking about are called "Roto Lock". You might be better replacing with same model from trane for the ease in base mount fit.
Mike T.0 -
Definitely okay
You will definmitely be okay with a 5 hp pump....There was an error rendering this rich post.
yes the fittings trane usually has are rotolock but this unit doesn't have rotolock. the suction and discharge are brazed on as most other manufacturers do it. so the only problem I'll have is mounting and some piping. so I'll go with the copeland instead of the original one trane used. It's about $350 cheaper.
professor silberstein said a any 5 hp scroll would be fine. I think he meant 5 ton. thank you0
- 123 Chimneys & Flues
