BASEBOARD ELEMENT
Paul S_3
Paul S_3 Member Posts: 1,291
WHAT IS THE LONGEST LOOP OF ELEMENT CAN YOU RUN WITH 3/4 AND 1/2 BASEBOARD?
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • billtwocase
    billtwocase Member Posts: 2,384
    You can run it to the moon if you have a circulator matched to it, required pressure, and pumping away. How long a loop are you running?
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,686
    To keep the average water temperature
    from going too low to be able to heat, I think you should keep 3/4" under 70 of element, and 1/2" under 25" of element. This would be on a continuous loop.
    Retired and loving it.
  • oil-2-4-6-gas
    oil-2-4-6-gas Member Posts: 641
    if you want to keep the rated btu output all the way to the end of loop typical high temp system i thought the limit was 65ft of element 3/4
  • Paul S_3
    thanks guys i figured it was around there....i asked a couple people they told me for 1/2 inch its 80 ft i guess they were wrong
    347-692-4777
    ASMHVACNYC.COM