low returns to new boiler
Charlie from wmass
Member Posts: 4,422
I think I know the answer but want to throw this to you guys to confirm. The boiler was replaced 3 years ago not by me. The new systems near boiler piping is a mess but I know that. What I am trying to figure is how to raise the water levels in the former wet returns. when the new boiler went in the far returns are now above the water line. I plan on causing a false water line by coming into the boiler room and jumping up before dropping to the return inlet at the Hartford loop. I will make sure the return is vented well so it does not siphon dry. But short of drawing pictures am I on the right track. I would prefer this to busting concrete or running 12 individual returns back to the boiler room so I can join them below the water line. The boiler room is 2 feet below the cellar floor and the boiler is a foot below the boiler room floor. No I do not have pics right now.
Thanks Guys for your input.
Charlie
Charlie
cell # 413-841-6726
cell # 413-841-6726
You will need to
equalize the top of the jumped-up pipe to the steam header. Follow the instructions and diagrams on pages 28-30 of Lost Art and you should be OK.
Thanks Steamhead I will look that up. the question now is , as it always is, do they want to pay to fix it properly or are they going to live with the issues.Cost is what you spend , value is what you get.
cell # 413-841-6726
Tell them
you guarantee results- it WILL work properly, no ifs ands or buts.
- 167 Indoor-Air Quality
