where can a diagram of a drop header be seen
Frank_63
Frank_63 Member Posts: 40
put images and links in your posts?
  • dave_151
    dave_151 Member Posts: 1
    drop header
    where can a drop header diagram be seen including the hartford loop connection and any special fitting's or devices,( trap,air vent etc.) that is needed for proper operation of the header.
  • Michael P. Bourque
    Michael P. Bourque Member Posts: 37
    Here is a drawing...
    Here is a drawing straight out of the Burnham Independence line of steam boilers.
    Click for larger size
    You definitely want to invest in a drop header. I am a home owner that got into a troubled install where the header the that was installed was all wrong. I did my research, and taught my installer how to do a drop header and what size pipes and their proper locations.
    See the discussion thread here
  • scrook_2
    scrook_2 Member Posts: 610
    Burnham I/O manuals
    The Burnham Megasteam I/O manual, page 23, has a nice diagram w/ both regular and drop header (alternate piping), plus both regular Hartford loop (Tee, close nipple, & 90° Ell) and Burnham preferred (Wye, close nipple, & 45° Ell) Hartford loop.
    http://www.burnham.com/PDF/IO/MegaSteam.pdf
    Alternately, see their Independence I/O manual, page 17.
    http://www.burnham.com/PDF/IO/Independence.pdf
    And here is a full view with hartford loop and equalizer
    I realized you wanted one complete view. So I took the boiler manual pics into photoshop and glued the drawings together so you can have one complete view.
    Click here for larger size.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    boiler fill
    one change i would make to that piping arrangement is to put the boiloer fill connection on the wet return, as far away as convienently possible, so as to avoid thermal shock, when filling with cold water.--nbc
    Ok - I edited the drawing to move the cold water feed
    Thats good advice to avoid shocking or cracking the cast iron. I edited the drawing and moved the cold water feed.
    See below.
    Click here for a larger picture.
    To post nice pictures inside your messages...
    1. Write your post
    2. Upload pictures as attachments, click ok
    3. Click preview button
    4. Right click the image links and pick copy image address
    5. Click re-edit post
    6. Add the picture in your post with this notation:
    <IMG width="450" src="image address">
    <a target="_BLANK" href="image address">Click here to enlarge</a>
    Where image address is the link you copied to the clipboard.
  • JohnNY
    JohnNY Member Posts: 3,341
    Dude....
    Dan doesn't want people to do that. It drives up bandwith and hosting fees. Use the attachment feature, please.
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes