dan holohans primary secondary piping works very well
wjp_2
wjp_2 Member Posts: 2
Looks good, but are those supply and return sensors located on the right part of the piping?
Thanks,
Jim
  • Chuck_37
    Chuck_37 Member Posts: 10
    primary secondary piping with weil mclain ultra PHD
    In the past we have had issues with how we piped our low mass boilers, but since i read dan holohans books life has been much easier and we have no more air trouble. here is a pic.
  • MikeyB
    MikeyB Member Posts: 696
    P/S
    Great work Chuck, any pics of the boiler? I'm looking to install an Ultra in the near future, thanks
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,686
    Nice to hear, Chuck.
    Thanks for the photo. Nice work!
    Retired and loving it.
  • Chuck_37
    more pics
    We have had great results with the ultra boilers. The only issue that we had was with the new control board, which is an easy fix. In years past we installed some modulating teledyne boilers which gave us nothing but trouble. The tech service was as bad as the boiler. But live and learn and find what works best for you.
  • Chuck_37
    Here are some more pics.
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,422
    Is that pex oxygen barrier tubing?
    cell # 413-841-6726
  • MikeyB
    pics
    Good stuff, thanks again Chuck
  • Chuck_37
    sensor location
    Jim I do beleive that the sensors are located per manufacturer specifications. However I'll let you know as soon as i get a chance.
    chuck
  • Chuck_37
    pex barrier
    Charlie, The wirsbo tubing absolutely has an oxygen barrier. We have heard of major issues with low mass boilers and the wrong tubing. I would not want to remove all of the tubing in a system like this one, I think we have over a mile of tubing throughout the house.
    Chuck
  • Dan H
    Dan H Member Posts: 15
    Ultra
    Couple of things.First the sensor locations are incorrect. They should be on your primary loop. Supply sensor just after the supply tee and the return sensor just before the return tee. It gives a distance in the manual but I don't have one in front of me to have an exact answer. There are already sensors internal to the boiler for the boiler supply and return.
    Secondly that is an Ultra series 3 with the U control. PHD was series 2 and a whole different monster. So far the series 3 is a better overall system but a little more touchy with popping up error codes.
  • Erich_3
    Erich_3 Member Posts: 135
    Expansion Tank Mounting
    Why is your expansion tank mounted sideways? The installation instructions clearly show that it is to be mounted vertically and state "Mount vertically only." The air valve is supposed to be on the downward side. At one time I called the company and they verified this information.
  • Chuck_37
    expansion tank positioning
    Erich, This is from the watts installation instructions. Perhaps other brands have different requirements.
    Series ET
    Non-Potable Water Expansion Tanks for Hot
    Water Heating Boilers and Systems
    Models ET-15, ET-30, ET-60, ET-90
    Series ET nonpotable water expansion tanks are designed
    to absorb the increased volume of water created
    when the hot water boiler is heated and keep the system
    pressure below the relief setting of the relief valve. Series
    ET is a pre-pressurized steel tank with an expansion
    membrane that prevents contact of the water with the air
    in the tank. This prevents loss of air to the water and
    ensures long and trouble-free life for the system.
    Note: Watts ET Series non-potable water expansion tank may
    be installed in a tee or any other suitable tapping in the heating
    system and can be installed in a vertical or horizontal position.
  • Erich_3
    Therm-X-Trol
    Chuck, your image shows a Therm-X-Trol expansion tank. That tank is made by Amtrol and the instructions call for a vertical mounting.
  • Chuck_37
    That tank would happen to be the plumbers tank. The gray larger Watts tank would be the one that I installed.