Thank you all for your responses. I think we have it closely figured out. I appreciate it.
water content
I'm trying to figure the amount of water contained in one sq. ft of radiation. Have a home that wants to anti-freeze their system and it has cast iron column radiators. Using Dan's EDR book, I can figure the sq. ft. of radiation but not the water content. Am I missing something? Let me know as I have a contractor that needs to anti-freeze this system today. TIA
Rick0 -
Well...
there is no usable relationship between EDR (which is a measure of effective surface area) and contained volume. Sorry about that...Br. Jamie, osb
You could
drain the system and measure.0 -
System volume
Rick,
You have to know your system pipe , boiler and radiators water content in gallons. When you know total system volume in gallons you have to use 70% water and 30% propylene glycol in the system. I have a table for pipe water volume, please e-mail me I will send this table to you.0 -
Howver there is some published data
from Burnham, from their "Hydonics Heating Helper" handbook.
Slenderized Radiators 0.066 gallons per EDR
Large Tube Radiators 0.106 gallons per EDR
Column Radiators: 0.188 gallons per EDR
Non Ferrous Convectors: 0.004 gallons per EDR
CI Convectors: 0.040 gallons per EDR
Radiant (SunRad): 0.066 gallons per EDR
Base Ray CI BB: 0.066 gallons per EDR0 -
and you will need
And you will need a much larger expanison tank!0