circulator pump orientation
Jay_45
Jay_45 Member Posts: 1
I am in the process of making some changes on an existing monoflow T loop system, it looks like it was installed in the 1960s or so. The venturi Ts are currently set up so that the CI radiator(s) return water is upstream from each corresponding venturi T. The return Ts are the regular type without a venturi. Is that something that was done by mistake?
Also, the system is currently pumping to the boiler and I want to pump away. In order for me to make this change I was going to relocate the Taco 007 pump, however in doing so I would need to mount the pump in a horizontal run. Is this OK to do with this pump?
Thanks in advance.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,369
    Venturi
    Yes the tee's were installed on the return riser of the radiator....
    You can install the circulator on the horizontal . Just make sure the motor is on the horizontal too. You can point it up if you maintain a high system pressure but if it were me I would not . Who want to....