steam heating system vapor stat controller
Options
c rafferty
Member Posts: 3
insatalled new boiler in a two pipe wet return steam heating system. when boiler calls for heat, the boiler fires for aprox 2 mins, then cycles off. does this about 8-12 times until tstat is satisfied. any sugestions on how to increase the cycle time. vapor stat is set at 8oz.
0
Comments
-
Vaporstat
Is it cycling with the Vaporstat? Or with the anticipator on the thermostat?0 -
What about..............
........the ever popular quick vents? If they're slow then the steam pressure at the boiler could rise to 8 oz. shut down and wait for the pressure to vent. test the vents0 -
vapor stat0 -
Vaporstat
Cycling on the Vaporstat before set temp suggests first that air can't get out of the system. Check your end of main vents.0 -
If it's a two pipe system with vents on the radiators then you don't need a vaporstat. you can use a pressuretrol and operate at 1 1/2 psi. Two pipe with vents and wet returns is not a vapor system.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements