steam heating system vapor stat controller
![c rafferty](https://secure.gravatar.com/avatar/b3be4eda680da8907c41fa0c3b16393a/?default=https%3A%2F%2Fvanillicon.com%2Fa9b34f335ede263ca1cc08c4953584a0_200.png&rating=g&size=200)
c rafferty
Member Posts: 3
insatalled new boiler in a two pipe wet return steam heating system. when boiler calls for heat, the boiler fires for aprox 2 mins, then cycles off. does this about 8-12 times until tstat is satisfied. any sugestions on how to increase the cycle time. vapor stat is set at 8oz.
0
Comments
-
Vaporstat
Is it cycling with the Vaporstat? Or with the anticipator on the thermostat?0 -
What about..............
........the ever popular quick vents? If they're slow then the steam pressure at the boiler could rise to 8 oz. shut down and wait for the pressure to vent. test the vents0 -
vapor stat0 -
Vaporstat
Cycling on the Vaporstat before set temp suggests first that air can't get out of the system. Check your end of main vents.0 -
If it's a two pipe system with vents on the radiators then you don't need a vaporstat. you can use a pressuretrol and operate at 1 1/2 psi. Two pipe with vents and wet returns is not a vapor system.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 101 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements