three pressuretrol on the boiler
akira
Member Posts: 1
Hi there
Here is a EU plumber who is truly fall in love with steam systems I learned a lot here too and of course every day (we don't have steam in Europe) anyway here is my question: recently I am working on a two pipe system and there are three pressuretrol on this boiler they all subtructive type honeywell Main on the right Diff on the left the very left one has no diff part the very right has rusted water all over it and a setting of 1 main 2 diff. I am pretty new to this but I figured this setting can not be right ( it says on the front SUBTRUCTIVE) I can not take 2 away from 1 right? So what would be the right ideal setting assuming everything else is running ideal. Thank you very very much. I would love to do it by the book. Have a great week.
Akira
Akira
Three of them?
that's called overkill on this side of the pond...
I'm sure one of the more knowledgeable will chime in (I hope) but -- I tend to set Pressuretrols 'by eye'; that is, I set the cutout (main) as low as seems reasonable (no more than two) and then set the differential so that the burner just barely restarts as the pressure drops on a cycle. Pressuretrols at low pressures being somewhat different, one to the next.Br. Jamie, osb
My guess is that one if for lo hi operation, one is operating
limit and one is safety manual reset limit. That is how we wire lo hi lo burners for steam boilers.0 -
Commercial steamers
are normally shipped w/ 2 pressure controls. Some installers, for some reason, install both + the required manual reset. That's the one w/ only 1 scale.
Some steam heat controls use a reverse, or a straight acting pressure control (or vaporstat), to start the heating cycle timing sequence.
Follow the wires.0
- 87K THE MAIN WALL
- 112 Chimneys & Flues
- 106 Geothermal
- 980 Plumbing
- 388 Solar
