'83 burnham p-206-w series 2
what's the lowest temp at which i can operate this old gal without creating a condensing problem? i'm running a tjernlund power vent
  • tim smith
    tim smith Member Posts: 2,886
    probably around 150 outlet temp on boiler depending on the delta
    t of system. Usually you want to not go below about 135 - 140 degree return temp.
  • hmmm, when i installed
    this system, i had approx 0 knowledge/planning, and not too much more real understanding now, so, bear with me on these questions
    i'm controlling it with a h-well L8148e, set at 180degs. with two circuits of staple-up and taco mixing valves, i can't keep the circuits lower than 130 and 140degs supply respectively. now, right after firing with the pumps running, and measured with a cooper contact thermometer, primary loop, my boiler supply is at 218degs and the return is 214. circuits as mentioned
    so here's what i think; i have more boiler than i need, and/or my pumps are too big/too little heat loss to the floors
    so, without making changes, new pumps/another zone/water heater, to the system, can i just lower the h-well to 160degs? would the boiler care, as long as the supply/ return aren't out of the 15-20deg drop?
  • tim smith
    Way too high, lower it to 155 to 160, should be much better.
  • thanks for the helpful
    and prompt responses. will do. and i'll keep you posted
    oops! the h-well doesn't have a setting below 180. looks like a new one is in order