'83 burnham p-206-w series 2
Options
[Deleted User]
Posts: 672
what's the lowest temp at which i can operate this old gal without creating a condensing problem? i'm running a tjernlund power vent
0
Comments
-
probably around 150 outlet temp on boiler depending on the delta
t of system. Usually you want to not go below about 135 - 140 degree return temp.0 -
hmmm, when i installed
this system, i had approx 0 knowledge/planning, and not too much more real understanding now, so, bear with me on these questions
i'm controlling it with a h-well L8148e, set at 180degs. with two circuits of staple-up and taco mixing valves, i can't keep the circuits lower than 130 and 140degs supply respectively. now, right after firing with the pumps running, and measured with a cooper contact thermometer, primary loop, my boiler supply is at 218degs and the return is 214. circuits as mentioned
so here's what i think; i have more boiler than i need, and/or my pumps are too big/too little heat loss to the floors
so, without making changes, new pumps/another zone/water heater, to the system, can i just lower the h-well to 160degs? would the boiler care, as long as the supply/ return aren't out of the 15-20deg drop?
0 -
Way too high, lower it to 155 to 160, should be much better.
0 -
thanks for the helpful
and prompt responses. will do. and i'll keep you posted
oops! the h-well doesn't have a setting below 180. looks like a new one is in order0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements