Thermolec Electric Boiler
Blackoakbob
Blackoakbob Member Posts: 252
I just had to say it. My 2 cents is that I pipe most of my electric boilers straight thru, but they are not Thermolec. If there is a chance that the smaller zone would run by itself then p/s would be best and if recovery is an issue a buffer tank would be good but I have mixed feelings about having a bucket of hot water just sitting around waiting ie. standby loss and space requirements. The electric boiler that I use has an outlet temp control and it works well with p/s or straight thru, it also has a 5-6 gallon capacity asme code vessel so it meets my applications well. Best regards,
  • Craig R Bergman
    Craig R Bergman Member Posts: 100
    Best option
    The Thermolec Electric Boiler's Install Manual is,at best, vague. The only information it really gives is a
    recommended flow rate of 5.2 GPM.
    The system requirements are... Zone 1 needs 3.8 GPM, Zone 2 needs 1.6 GPM and Zone 3 needs 2.6 GPM. Required water temp is 125*.
    Would Primary/Secondary or a Buffer Tank be the best option for this Electric Boiler?
    Bergy
    hot_rod Member Posts: 26,575
    As I recall
    that boiler has 1, maybe 1-1/4" connections into the HX. It should be able to flow 8gpm if 1" maybe 12 if 1-1/4".
    Usually they will flow the gmp equal to their output as a 20 KW (20 x 3.41) should flow 6.8 gpm.
    Most electric boilers are just a tank with elements screwed in. although the instantanous water heaters discuised as boilers have some flow restrictions.
    the Electromn.com is another nice electric boiler to consider.
    hot rod