no flow
Jim_47
Jim_47 Member Posts: 244
What has been the outdoor temp in that area lately?(frozen pipe in an out of the way location?)
What is the system presure on your gauge? Not the system gauge. NEVER belive the system gauge. makeup a gauge 0-30 or 0-50 lb gauge on a hose thread adapter and put it on a boiler drain. MANY hydronic problems can be cured with the correct pressure.
  • Steve Gates_3
    Steve Gates_3 Member Posts: 27
    no flow
    No heat call in one zone. Check circ and can stop vanes with a finger. Install new 15-58 w/out check. No flow. Check spinnig vanes can't stop as easy as old one. Inline springcheck seems to be ok.
    System has been up and running for 4years.
    Don't believe it's an airlock but bleed some anyway, thought had est. flow and leave. NOPE.
    Brain stall. Now what?
  • Brad White_184
    Brad White_184 Member Posts: 135
    Power
    Dumb question but is it operating? Power to it? Polarity (forward versus reverse?)
    Closed valve or blockage? Just fishing here and sorry to seek the obvious as you probably already have.
  • Steve Gates_3
    Yes,yes and forward. No closed valves(that I know of and I installed it). Manifold valves still open because they can't be reached.(without a sawzall)
    Stilled stumped
  • Steve Gates_3
    As low as -6. Not frozen cause I purged some. 20psi on two gauges. System is two vito's, two temps, ODR, and my h/b gauge is being taken off another system that froze today( I use that thing alot)
    Thanks
    and stilled stomped
  • Weezbo
    Weezbo Member Posts: 6,231
    this is way likely,...
    the first go around the circ may have been contributing to a low flow condition...maybe... then after the new circ ,no flow. it sounds too much like the circ is installed against the previous flow direction ... and possibly pumping "Against"
    seated check or much larger system head..