any tips on running a radiant loop off a steam boiler?

Options
If it is not being used for domestic hot water. They make coils with 3/4" tappings for this purpose. I did one that way and it worked great, no worries about sediment.
Thanks, Bob Gagnon

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=331&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
To learn more about this professional, click here to visit their ad in Find A Contractor.

Comments

  • jrob
    jrob Member Posts: 1
    Options
    radiant loop off a steam boiler

    any tips on running a radiant loop off a steam boiler?
  • Norm Harvey
    Norm Harvey Member Posts: 684
    Options


    Definately use a plate exchanger with the circulator and exchanger protected by a wye strainer and bypass

    There was an error rendering this rich post.

  • Canadasteam
    Canadasteam Member Posts: 13
    Options
    radiant loop off a steam boiler

    Add sediment faucets to steam in and condensate out ports on your heat exchanger, to allow flushing of mud out of the small galleries within the plate type heat exchangers.
    Shell and tube type exchangers have less fouling problems but are larger in size and more expensive.

    Good Luck
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,530
    Options
    Yes.