Pressuretrol vs. Vaporstat
gerry gill
Member Posts: 3,083
operates in pounds, the vaporstat operates in ounces.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=360&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
gwgillplumbingandheating.com
Pressuretrol vs. Vaporstat ????
What is the difference between a Pressuretrol and a Vaporstat? Is it reliability? Operability?0 -
I might add
to Gerry's remark that they also operate in different pressure ranges. The vaporstat will reliably, repeatedly, operate on pressures as low as a few ounces; a pressurestat, generally, becomes unreliable if you try to set it much below a pound or two. Since most steam heat systems operate on no more than say 10 to 12 ounces...Br. Jamie, osb
- 167 Indoor-Air Quality
