The specs for the pa404a with additive differential are here:
http://tinyurl.com/35t5he
The diff available is 1 to 5 psi.
Resident in 25-unit co-op, Toronto, built in 1925. In self-defence,"expert" on our 2-pipe steam system.
pressuretrol adjustments
Good morning
I have a honeywell PA 404a pressuretrol. It was set at .5 cut in with 1.5 diff.
I was trying to adjust the white differential wheel in the box however it stops at 1. is this the limit for this ?
Seems that I can only adust down to 1.5. cut in plus diff equal cut out.
One pipe system.