pipe size & edr
Brad White
Brad White Member Posts: 2,399
I am assuming this is one-pipe steam?
Is the EDR SF served by each 2-inch main roughly equal? Does either one exceed the 386 number by much if at all?
I do not see a problem.
The header from which the 2-inch lines emanate should be larger than 2-inch. I would expect that to be at least 2-1/2" if not 3-inch size.
Not sure I grasp the issues you are concerned with, otherwise.
"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad
  • Dan_43
    Dan_43 Member Posts: 58
    limitation of the main in a one pipe steam system
    I am replacing my boiler and I have read in Dan's book that a 2" main's maximum capacity is 386 sq-ft of steam.
    I need based on the radiator load 540 sq-ft. I have (2)mains coming from the header. Is the math 2 x 386 and therefore that is why my system can handle the 540 because each main will only have 270 sq-ft of steam in each main.
    It makes sense to me! how about you all?
    Dan
  • Dan_43
    your question answers mine
    thanks
    Dan