water water zone off of a steam boiler
HTP uses this one, too.
Noel
  • kevin nagle
    kevin nagle Member Posts: 3
    hot water zone off of a steam boiler
    We installed a burnham v83 steamer inplace of a peerless jot 3 section, that had a pressurized coil for the upstairs of a cape cod with baseboard and 4 rooms .
    We ran a zone off the bottom of the boiler in place of this. It came back with not enought heat---- Here's how we piped it----came off the bottom of the front of the boiler with a taco 007 then a inch flow valve then the feeder teed in then 3/4 pipe for the supply, so when the boiler feeds it has to purge the zone also.
    on the return we first had purge set-up in 3/4 then a inch flow valve into the inch tapping just below the water line---note it was very hard to purge it.
    what's wrong--------KN
  • TJ_5
    TJ_5 Member Posts: 71
    Hot water zone on Steam system
    If you go to the Systems section and Hot water section there is a very good recepy to make this work for you.
  • hot water loop
    off a steam boiler, I just finished one last noght and I piped it from a diagram I found in the library on this site. It worked great. Bob Gagnon
  • This diagram, Bob?
    Zone Heating with Condensate
    Noel
  • Kevin
    When you say upstairs , do you mean the 2nd floor ? There is a finite height you can go , piping it off the bottom . Does anyone know this height ?
    We always try to use the coil and pressurize the zone when it's higher than the boiler itself . Too many headaches from going off the bottom .
  • Noel
    That's the one. Did you write that up? Good job if you did. Thanks, Bob Gagnon
  • Joey B_2
    Joey B_2 Member Posts: 24
    When using a coil for a BB zone what are your limitations? I've never seen a zone piped out of a coil before. Do you need a particular type of coil or is it a regular domestic coil?