Ran across a GB 142 with a fairly crusty heat exchanger the other day. I've heard you use mineral oil but not sure how you go about it. Thanks for any tips.
  • The Kid_2
    The Kid_2 Member Posts: 19
    gb cleaning
    Check this link detailed instruction, from the buderus website.
    http://www.buderus.net/LinkClick.aspx?fileticket=0cgZCcY9YoE=&tabid=108&mid=646
    Chapter 13.1
  • Derheatmeister
    Derheatmeister Member Posts: 1,659
    Have a BBQ
    Turn gas and electric off
    Remove the top and the bottom access panels
    Remove the buckets and deteriorating Aluminium
    Take a soft brush and brush the Mineral oil onto the Heatexcharger (Think BBQ Chicken wings)
    Grab a beer
    Fire up the boiler and let it go for about 30 Min.
    Turn off the boiler and let it cool down..Trink more Beer but stay within the 2 beer limit.
    Open the BBQ, Oh no i mean the Boiler!
    And clean out the Derbies kinda like cleaning out you BBQ.
    DO NOT CLEAN IT TO GOOD OR EXPOSE SHINY ALUMINUM!
    as the Corrosion process will gain on your exchanger!!
    Close everything back up.Fire back up and check combustion with a analyzer..
    If you did not install it, Charge accordingly because it's not yours..
    This can take a couple Hours
    Again Think BBQ Hope this helped Richard from Heatmeister..