CONVERT STEAM TO VACUUM
Options
WAYNE M
Member Posts: 7
CUSTOMER HAS AN APARTMENT BUILDING THAT WAS VACUUM SYSTEM 25 YEARS AGO WE CONVERT TO LP STEAM SYSTEM. LOOKING FOR A SIMPLE, NON MECHANICAL WAY TO CONVERT BACK TO VACUUM WITH OUT VACUUM PUMP
0
Comments
-
If that's the typical
2-pipe vacuum system, and it was designed for vacuum originally, the piping is sized for the greater ∆P the vac pump would deliver. So without the pump, you likely have distribution problems, banging etc.
First thing to do is fix the leaky traps. These were probably what killed the old vac pump. Then see where you stand.
If you still have parts of the building that don't heat well, you'll need to put a vac pump in.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0