Munchkin delay ignition, Help
tim smith
tim smith Member Posts: 2,886
Mark, yes i do have all and know how to use them but this unit has been in operation for 1.5 years but all of sudden last night it started delaying on ignition and I can't get it to run to check combustion.
  • tim smith
    Munchkin delay ignition problem.
    See post below for details, rather that rewrite them. Thanks Tim.
  • Mark Eatherton1
    Mark Eatherton1 Member Posts: 2,542
    Tim...
    Do you have a combustion analyzer, a magnehelic gauge and a manometer? If no, then I can't help you. If yes, do you know how to use them?
    These instruments are required to check critical parameters and are USUALLY carried by professional service people. If you don't have them, you may need to wait until tomoroow to contact someone who does.
    This ain't your Grandpas Buick anymore...
    ME
  • S Ebels
    S Ebels Member Posts: 2,322
    Wellllll lesss'eeee
    If it wouldn't run long enough for me to take a read on anything I guess I'd yank the burner and start with a good cleaning. I'm guessing the burner, flame sensor or the HX itself are fouled up with some type of crud. Check the condensate drain, I've had more than a few plug and back water up into the combustion chamber. Could also be the ubiquitous "mouse turds".
    Does it light at all or just go through the motions?
    Any failure codes flashing?
  • Rely_2
    Rely_2 Member Posts: 61
    firing problem
    How is the flame rod on the unit? and call the utility company and see if they lowered the btu contant of the gas in that area spring is around the corner and we may have shortage so why not lean it out no one will know ha ha.You got to love it.With n gas being the way it is I see o2 sensor on the exhaust coming soon.
  • Wayco Wayne
    Wayco Wayne Member Posts: 615
    Interesting
    I was thinking the same thing the other day. Cars have Oxygen sensors why not boilers. Why not a boiler that adjusts itself to the btu content of the gas? I wouldn't be surprized if one is already in a lab putting away. Making it affordable is probably the bigger problem. WW
  • tim smith
    response to steve
    Steve, that is the first thing i did. Cleaned flushed etc. I would try to light at the very end of the trial w/ valve open, then bangggggggggggggg. Neighbor heard it saturday night from 2 blocks away. Thought it might have been gun shots? Ps, very slight mouse turd build up and no signs of condensate build up.
  • Rich S_2
    Rich S_2 Member Posts: 2
    Booming Munchkin
    Could the combustion chamber have gotten wet? The gasket between the burner and the combustion chamber access cover can disintegrate when wet, allowing gas to escape and delayed ignition.
  • R. Swatton
    R. Swatton Member Posts: 86
    Check the spark igniter. The gap could be out of adjustment giving it a delayed ignition (thicknes of 2 pennies).Also re-test yor CO, sometimes for unknown reasons it can drift due to gas quality, gas air mixture. Also check the burner gasket.