Drip line causing water hammer - how to resolve
rich pickering
Member Posts: 276
The pipe was changed as part of a rework of the condensate pipe. Instead of a direct run to the condensate pipe, the drip runs another fifteen feet.
I have some photos I can post tomorrow.
I have a drip line at the end of a main that connects to the condensate line. When the system runs and steams, there is loud hammer pounding when the drip line starts flowing into the condensate line. The condensate line feeds a boiler feed tank. There are no traps. The system pressure is 8-oz.
Any suggestions on how to quiet this down? The pipe is new and pitches more than adequately. The pipe has three 90* elbows on the way to the condensate pipe.
Thanks,
Steve0 -
When was the pipe changed and was it replaced as it had been or modified? Size changed, pitch changed? Was the pipe reamed? Any pictures?Cost is what you spend , value is what you get.
cell # 413-841-6726
Looking forward to pictures
but in the meantime, is there a long or longish horizontal run in the new drip which is above the water level? I can't, off hand, think of any where else you could get a slug of water moving fast enough to make a hammer except in such a long line... if so, is there any hope of lowering it so it is always full of water?Br. Jamie, osb
Yes, the drip now has a horizontal pitched run of roughly fifteen feet.0 -
Photos
Here are the photosSteve from Denver, CO0 -
The pipe in the photo runs around 30inches to a 90* elbow going right for eight feet to another 90* elbow going right to a last 90* elbow to the condensate pipe. The pipe has a good pitch for the entire run.0 -
Jamie:
It is a longish run that is horizontal. You can hear the condensate dripping/running down the pipe. And since it isn't full, you know there is also steam in the pipe.
Is this a situation where a trap is needed?0 -
so do i have this right?
are you telling me that that little **** pipe is handeling both start up condensate load from the steam main, and steam also since you said its going to a feed tank..if the feed tank is vented, then isn't steam free to push air out that dinky pipe, then the steam enters the pipe along with all the condensate..if the air can get out the steam will go in, right? from your description, which i hope is wrong, and your picture, i don't see how it cannot help but to hammer.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"gwgillplumbingandheating.com
Gerry:
I should clarify: that little pipe is the drip that is below the take-off to a five foot long radiator. The steam main continues another five feet and then drops to the condensate pipe.0 -
Not a gamblin man
but I'm going to be that that horizontal run above the water line is your problem. Even if it is well pitched, I can easily believe that you could get slugs of water in there being pushed by high velocity air or steam, and wham-o.
I don't see a decent solution except to lower that run so it is below the normal boiler water line (bring a longer vertical leg down from the main to below the water line, THEN run the horizontal to where it needs to go. Maybe there's a better way... but I doubt it. I don't think a trap will help...Br. Jamie, osb
Might a larger pipe for the drip help? Or would it be a crap shot?
Another thought: the main return leg for the main is just four feet away. Perhaps we should try plugging this drip and see if it lessens the hammer, or simply makes it worse but in a different place.Steve from Denver, CO0
- 167 Indoor-Air Quality