Refrigeration pipe sizing
Geno54_2
Member Posts: 1
The capillary/expansion device is on the outdoor section / condensing unit. What you see as the liquid line is actually the beginning of the evap. Hence the need to insulate both lines. Have seen some confuse this and install liquid line driers. That is a no no on most ductless splits. 410a mimicks r-22 for pipe sizing. Haven't gone wrong using them yet.
Refrigerant pipe sizing
I'm looking for pipe sizing charts for 410A and 134. Have all the others. Anyone know where to look?????????????????
Thanks,
ED0 -
Thanks,
ED0 -
Never saw a difference
for 410A,might want to check with the manufacturer and see what they have to say.0 -
I had asked this
about six months ago and came up empty on R410A. What I have seen in the field at least is that the sizes, even over good distances, seem a tad small from what my gut says would be ideal. They seem to be "connection size" if not, then "connection size plus one". Still, the systems work but I am specifically NOT giving this as sizing advice. It is just what I have seen and is hardly the last word. Far from it!
The manufacturers I have spoken with (Mitsubishi and Daiken being but two and regarding their VRF type systems), have given me blank looks but then point to their sizing and design software showing, routinely, 130 foot runs of 3/8" liquid and 1/2" or 5/8" suction lines for a ton or so worth of evaporator.
For 134A, I have that in my tables and sizing program. If you have a specific application, fitting count and lengths, I can spot you a sizing run if you like.
But 410A? I would love to have a good set of charts...0 -
this
This should help.
http://www.suva.dupont ca/pdf refrigepiping-engineerpdf.
http://www.refrigeration piping%20sizing.0 -
R-410a pipe charts
Hi Brad!I have this 3-chapter,"Application Guide" in Chaptr 1 ,page 16 there is this "Liquid Line Selection Table For R-410A Systems" chart and on paqe 17 there is this "Allowable Suction Line Diameters and BTUH Loss(R-410A)" table.Sound like a possibility? Terry.
Terry
Hey, if that is not a copyrighted work, I would love a copy of the charts but if you have a publication number, I might be able to get a fresh copy- Thanks!
Brad0 -
410a Tables
Good Morning EBEBRATT ,Brad!I remember that thread from 6 months back, Well, anyway,no Copyrighting infringements here.Your local Trane distribuator should be as helpful as was mine.It's titled "Application Guide" and"American Standard 2000" is on the Index page, and the number 32-3009-93 is also there .
Ch-1 -Refrigerant Piping.
Ch-2 -High Rise Applications,
Ch-3 -Hot Gas Bypass
Let me know if this what you are looking for!0 -
Link Won't work
Don,
I can not get those links to open when I cut and paste them.
Could you try to post them again
Thanks,
Ed Carey0