Radiant Mixing -VS- Temperature Sense
adayton_2
Member Posts: 130
valve like Taco RMB is an excellent solution for a new full/large installation. But.. for a small retrofit of a single room (20 x 20) would there exist a solution to do the following: replace existing Honeywell aquastat currently set to fixed 160* to a "variable temp" Aquastat that would be controlled by an outdoor temperature sensor? That is when the outdoor sensor sees the temperature drop in discrete steps that would have a SIMPLE (i.e., inexpensive) control INCREASE the aquastat setting. Obviously the reverse would hold true, increase outside temp would cause the control to drop the aquastat setting. aquastat is ONLY being used for this radiant heat and to maintain boiler standby for steam heat which would only incidentaly benefit from the same control condition. Taco and other RMB's run $700 and up which is a bit much for this simple "low cost" application. Would consider other approaches also such as replace existing standard Taco circulator with variable speed circ that would "sing" in tune with the outside temp... :-)..Alfred/Jim
Taco
iSeries 2 and 3-way mixing valves will do what you want.
http://www.taco-hvac.com/uploads/FileLibrary/iSeries_S.pdf
Joe Mattiello
Technical Support Technician
Tel. 401-942-8000 X 484
Fax. 401-942-2360
1160 Cranston St
Cranston, RI 02920
joemat@taco-hvac.com0 -
Taco radiant made easy application guide
There are several options for radiant systems. For a great reference guide visit www.taco-hvac.com click on products, radiant systems, click on the Taco radiant made easy application guide.