peerless boiler
ralman
Member Posts: 231
I checked and set to 12 PSI before filling system with water. It will be very difficult to remove all those tees. I posted a different question after this one about using pex tubing to connect the supply and return tees together. What are your thoughts?
peerless boiler
I have a peerless boiler model ec 103 oil fired water boiler. there is a tapping on top of the boiler for air elimination but it is plugged. what if any air eliminating device should be installed in this tapping? The boiler is connected to a single pipe monoflo tee system with mostly cast iron baseboard. The supply pipe runs to a tee on one side of the home and follows the perimeter of the home where the two pipes join back together with a y fitting. There are balancing valves on these 2 return pipes. I did not know they were balancing valves and turned them fully open. The only means of air elimination is the baseboard vents. There has been 6 baseboards removed and capped off by previous owners.The circulator is on the return pipe. I drained the system to replace a faulty pressure relief valve. I have been having difficulty filling, bleeding and balancing the system. Questions are: Should the circulator be moved to the supply pipe? Should the capped monoflo tees have a pipe placed between them? What is the method to fill, bleed and balance?0 -
Time for a pro
Without seeing your system it is impossible to tell you how to get the system running smoothly. If you have your heating company come in and bleed the system they can show you how to balance it.
David0 -
Monoflor?
> it.
> David
Air elimination
on a monoflow system is very difficult. You need to install a proper purge assembly along with a air elimination device and while you're at it, switch the circulator to the supply line and "pump away" from the expansion tank. You might also consider primary-secondary piping to keep the boiler happy.
Any knowledgeable heating contractors in your area?
Thanks for your advice
I have had 2 different heating companies come out and they really haven't been able to take care of this problem. From what I have been reading My system seems to be improperly piped. The house is 50 years old, the piping and baseboards look original. I am guessing it was originally a coal boiler and I see evidence that there may have been a natural gas boiler before this oil boiler was installed 5 years ago.0 -
The capped monoflo
tees are a no no, I would remove them. The plug in the top of the boiler? It depends on what type of compression tank you have, if it's conventional you don't want any automatic air vents. bob0
- 121 Chimneys & Flues