                    Plumdog_2                
                
                    Member Posts: 870                
            
                        
            
                    on two-stage outfit. One blower speed stayed hot all the time while other one came on as well. So; can you check resistance thru windings to see if they are in spec?                
                0                
            Comments
- 
            Testing Blower Motors
 What's proper way to test shaded pole 1/3 hp 3 or 4 speed blower motors to determine suitability for continued use? I have amprobe, digital voltmeter, etc. Had one wired hot to two speeds at once and draws big amperage now. Smells like electic toast.0
- 
            
 Well, I guess you won't do that again. Replace the motor--you've compromised the windings. Not today, maybe not even tomorrow. No, that motor will die when it's the least convenient time for you and/or your customer. And remember--experience is what you have right after you needed it.0
- 
            I agree
 with charles them motor dont smell nor taste good when you have to eat them.
 But hey remember you can only eat two.LOL.
 I had fan relays that would not open the normally closed contact on fan relays and burn out a newly install motor.
 Just when you assume Mr murphy is always there to greet you.
 Welcome to the club.
 0
- 
            Sounds like...
 Sounds like you partially shorted a winding...
 Shorted winding = reduced resistance = increased amperage = more heat generated = more damaged windings = more severe short circuit = higher amperage = a bad thing
 The moral of the story is... Never energize more than one motor speed at a time!0
This discussion has been closed.
            Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements