Testing blower motors

Plumdog_2
Member Posts: 873
on two-stage outfit. One blower speed stayed hot all the time while other one came on as well. So; can you check resistance thru windings to see if they are in spec?
0
Comments
-
Testing Blower Motors
What's proper way to test shaded pole 1/3 hp 3 or 4 speed blower motors to determine suitability for continued use? I have amprobe, digital voltmeter, etc. Had one wired hot to two speeds at once and draws big amperage now. Smells like electic toast.0 -
Well, I guess you won't do that again. Replace the motor--you've compromised the windings. Not today, maybe not even tomorrow. No, that motor will die when it's the least convenient time for you and/or your customer. And remember--experience is what you have right after you needed it.0 -
I agree
with charles them motor dont smell nor taste good when you have to eat them.
But hey remember you can only eat two.LOL.
I had fan relays that would not open the normally closed contact on fan relays and burn out a newly install motor.
Just when you assume Mr murphy is always there to greet you.
Welcome to the club.
0 -
Sounds like...
Sounds like you partially shorted a winding...
Shorted winding = reduced resistance = increased amperage = more heat generated = more damaged windings = more severe short circuit = higher amperage = a bad thing
The moral of the story is... Never energize more than one motor speed at a time!0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 67 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements