Sys. observations
![[Deleted User]](https://secure.gravatar.com/avatar/a286b777013a82fb0a96d64122122145/?default=https%3A%2F%2Fvanillicon.com%2F5385664c61e6a76e78b466751687bd8c_200.png&rating=g&size=200)
[Deleted User]
it looks like you are exposing your boiler to the serious potential of condensate production, which is not good for an appliance that was not designed for it.
ME
ME
Tonights activity
What would be your thoughts on my systems cycles?? the house is nice and warm and the bills are not bad.
Outside temp. 5°F, Inside 70°F
1947 2 story, no insulation on main floor, leaded glass windows, Gravity conversion, boiler bypass.
ON - 7:45pm, Sys. temp 100°F, stat, 70°F
OFF - 8:22pm, Sys. temp 125°f, stat, 70°F
Delta T - 15°F
Run time - 37min
Off time - 27min.
ON - 8:49pm, Sys. temp. 105°F, stat, 70°F
OFF - 9:26pm, Sys. temt 130°F, stat, 70°F
Delta T - 15°F
Run time - 37min0 -
I should have included more details.
Sys. temp is mixed temp. from boiler supply and return. boiler gets over 140-180°F depending on the weather and if I've fiddled with the bypass or not.0 -
Sounds quite reasonable to me. Judging by on-off times, you're operating at about 2/3 of boiler capacity. How was outside temp compared to design outside temp?
Also looks like a nice and clean gravity conversion. Compression tank looks rather small, but considering how nice everything else looks, I'm sure you sized it properly for the volume of your system.0