Pump Control Based on OA
Options
Matt_49
Member Posts: 4
I have a hot water heating system with two constant speed pumps set up in a lead lag control fashion. No DDC, all stand-alone controls. During very cold days, when all the control valves open, I get a very large supply and return water delta T and not enough heating capacity. I would like to use a controller that will bring on the second pump to run in parallel based on outdoor air temp.
Does anyone know of a controller that will work?
Does anyone know of a controller that will work?
0
Comments
-
Johnson A419
What about a simple setpoint controller like the A419?0 -
That or a Ranco ETC
Anything simple as these will work. I prefer external thermistor sensors. The Ranco ETC also has a two-stage model so you can set it up in a variety of ways."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements