Pump Control Based on OA
Matt_49
Member Posts: 4
I have a hot water heating system with two constant speed pumps set up in a lead lag control fashion. No DDC, all stand-alone controls. During very cold days, when all the control valves open, I get a very large supply and return water delta T and not enough heating capacity. I would like to use a controller that will bring on the second pump to run in parallel based on outdoor air temp.
Does anyone know of a controller that will work?
Does anyone know of a controller that will work?
0
Comments
-
Johnson A419
What about a simple setpoint controller like the A419?0 -
That or a Ranco ETC
Anything simple as these will work. I prefer external thermistor sensors. The Ranco ETC also has a two-stage model so you can set it up in a variety of ways."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0