Tekmar 260 controler
JohnNY
Member Posts: 3,389
Do you have power at the 'boiler demand' terminals (1 and 2)?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=290&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
Classes
tekmar 260 controler
Im having problem with a tekmar 260. The controler is running an oil fired buderus gs115 w/ a beckett burner. The boiler runs great best burner I ever worked on. The problem is the controler will not read a boiler target temp. It just shows ---- across the screen. If i make an adjustment to the DHW tanks aquastat the unit will reset it self and and then start the main circulator and fire off the boiler. I think there is a problem with the prioety setting with this controller but i do not want to condem it untill Can get some second opions Thank you.0 -
Ohm the sensors?
Did you ohm your supply sensors and your outdoor sensors to make sure they are both reading correctly?0 -
tekmar260
I have no readings at the boiler demand points. I also ohmed the sensors and get nothing. I am using a digital fluke I have to find another meter to recheck the ohms.0 -
1 and 2
You've got to bring power to 'boiler demand'. Anywhere from 12 to 240 volts, if I'm not mistaken.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Classes0 -
I'm with Wheels.
Ohm out both sensors.(boiler feed and outdoor) I've run across a few bad sensors in the last 5 years. Rare, but definately possible.
Question B, Do you REALLY need it to be in "priority"?, Sometimes it ain't the best way to go...but sometimes it's needed. I like to raise the indirect temp. and mix down. It has the effect of having a larger tank, and with the 260,and a good setpoint controller(say Tekmar 150) you can adjust the differential on the water heater to avoid any conflict. JMHO. Chris0 -
tekmar 260
I traced out the boiler demand and it runs to X1 on an ArgoAZV 244P zone valve board. The board is powered up with three zones calling but I have no power at X1 or X2.
Prioirty
I shut off the Priority swith on the controler. I was watching it cycle and the board was constantly calling for the DHW pump to run and not letting the main circ run. I know this is what the priority set up does but I think I need it to run the circ going through the indirect tank on the system. I toyed with the idea of installing a zv in place of the circ but it a lot of work and I dont know the wieght of the gain.0 -
I gotta believe that's the problem.
See if you can bring power to X1 (isolated switch, right?) fro m either L1 or a 24 volt source.
Either way, you've just got to get a power source, the isolated switch and the boiler demand terminals in series to form a complete circuit.
Classes0 -
tekmar 260 Boiler Demand Wiring
Hello,
As explained above, run L1 to one side of X1. Then a wire from the other side of the X1 to Terminal 1 on the 260, followed by a wire from Terminal 2 on the 260 to Neutral.
110Vac power is switched through the ARGO X1 terminals to energize a Boiler Demand (Relay Coil) in the 260 Control.
Hope this clears it.
Regards,
MikeThere was an error rendering this rich post.
zero ohms or infinity?
what i have seen "---" means the sensor input is "open" or sensor not connected/broken. check wiring too.0 -
tekmar 260
I found the Argo board was not passing voltage through X1. I also found one of the leds were burnt out. I think the board reached its end run. I replaced the argo with a Taco board and now the system is back on line. Thank you to everyone who responded.0