commercial convectors
Tim_33
Tim_33 Member Posts: 83
A "fan assisted" convector, is more commonly known as a cabinet unit heater. Other manufacturers are McQuay, Modine and Reznor.
  • Bruce_17
    Bruce_17 Member Posts: 7
    Who makes them for hydronic heating and do they make them with an output in excess of 40K Btu/h, fan assisted of course. Wall mounted.
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Many manufacturers
    Airtherm, Sterling, Trane, Vulcan are the ones I specify most often. What water temperature are you running?
    At 180F supply water, 20 degree drop, a Sterling 10 with a standard coil will do the job (41.5 MBH output) at 4.0 GPM and low speed. Unit is 66" long, 9.5" deep and 25" high.
    The high capacity 2-row coil model will do the job in an 06 size (40.9 MBH output) at 2.0 GPM (40 degree drop- cool!) Dimensions are the same as the #10 except length is shorter at 59 inches.
  • Ron Schroeder
    Ron Schroeder Member Posts: 995
    Brad
    Thanks for the answer but just so you know it was not this Bruce that asked, didn't want you to think I was being inappreciative of you answer.