Patterson-Kelley
Todd_31
Member Posts: 4
The ones I have seen have all been the Mach series. AS for the one that our company installed, it was set up by a company rep.
Patterson-Kelley
I'm seeing these boilers popping up in my area. Our company has installed at least one of them. Do any of you Wallies have first hand experience with them?0 -
dependning on the model -if its the THermific --rectangular unit 5ft high --if you dont set-up the burners' screening can get burned out --clean the intake fan and screen on a regular basis -- they can be sensitive with the pilot electrode and flame-rod --make sure you leave spares on site ----if you service older 1s and you get rumbling -pull the burner assy.check for cracks in the screening -- FOLLOW the clearance guidlines -for the outside and top of the unit --for future service --0 -
P& K boiler
We have a couple of these units they are very dependable if kept clean and set right at specs0 -
Made in USA
ME(Mark)and i installed 2 X 1.700 000 BTU PK Boilers on a snowmelt system up here in Colorado.
As far as i remember a company rep came out to help adjust these babies.
Venting was custom order.
At first i was skeptical about the CU exchanger!
After 2 years i serviced them and found that they were still pushing the 90+ efficiency and clean as a whistle.
If you are looking at the Mach series be aware of the Aluminum and the Requirements thereof
Which ones are you looking at?
Made in PA ! This is a good American Company!0
- 109 Chimneys & Flues
- 5.6K Gas Heating
- 969 Plumbing
- 385 Solar
