low level CO detectors
The NSI 3000 low level CO Monitor exceeds the UL 2034 rating.
The screen will show 5ppm and sound the alarm at 15ppm after it has measured 15ppm for 15 minutes. It is only sold to contractors.
www.nationalcomfortinstitute.com
  • Dan C._2
    Dan C._2 Member Posts: 54
    I am looking for
    a low level CO detector that meets all of the following requirements. Does anyone know where I can get one or if there is one that even meets these requirments? Thanks
    If there is no carbon monoxide detector with an alarm already installed in
    compliance with the most current edition of NFPA 720, NFPA 70 and the
    Massachusetts State Building Code in the residential unit served by the side
    wall horizontally vented gas fueled equipment, a battery operated carbon
    monoxide detector with an alarm shall be installed in compliance with the most
    current edition of NFPA 720, NFPA 70 and the Massachusetts State Building
    Code.
    2. In addition to the above requirements, if there is not one already present, a
    carbon monoxide detector with an alarm and a battery back-up shall be installed
    and located in accordance with the installation requirements supplied with the
    detector on the floor level where the gas equipment is installed. The carbon
    monoxide detector with an alarm shall comply with 527 CMR, ANSI/UL 2034
    Standards or CSA 6.19 and the most current edition of NFPA 720. In the event
    that the requirements of this subdivision can not be met at the time of the
    completion of the installation of the equipment, the installer shall have a period
    of thirty (30) days to comply with this requirement; provided, however, that
    during said thirty (30) day period, a battery operated carbon monoxide detector
    with an alarm shall be installed in compliance with the most current edition of
    NFPA 720, NFPA 70 and the Massachusetts State Building Code. In the event
    that the side wall horizontally vented gas fueled equipment is installed in a
    crawl space or an attic, the carbon monoxide detector may be installed on the
    next adjacent habitable floor level. Such detector may be a battery operated
    carbon monoxide detector with an alarm and shall be installed in compliance in
  • Rudy
    Rudy Member Posts: 482
    Unfortunately
    There is no such thing as a low level, UL-2034 approved alarm.
    UL requires that an alarm never display/alarm below 30ppm nor alarm between 30ppm - 70ppm although it can display.
    Since UL does not require any degree of accuracy of the display, however, that doesn't help much either.
    The GRI report on the Performance and Reliability of CO alarms noted that the digital readouts seems to be displaying random numbers....
  • Rudy
    > 2034 rating.
    > contractors.
  • Rudy
    OK
    Odd thing is that if it 'exceeds' the requirements of UL 2034, then it is not 'approved'....
    go figure