Purging Monoflo/Glycol Job
Ragu_5
Ragu_5 Member Posts: 315
Going to an old house next week to separate the first and second floor into 2 zones. The whole house is convectors and they are piped with diverter tees (thanks, Dan!) and there are air vents on all the convectors. This is a glycol job so I'll be using my purge pump. Circs are on the supply. Any time-saving purging tips? Thanks.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=428&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
  • Pinball
    Pinball Member Posts: 249
    Purge and bleed with plain water in the traditional way first. Then,when all the air is out, add the amount of A/F you need. 1 gal A/F in = 1 Gal of water out. until you get the mix you are shooting for. generally 35% but no more than 50/50.
    Al
  • Ken_40
    Ken_40 Member Posts: 1,310
    And then...
    After being certain the entire system has no air left, take a few ounces out and check the protection level with an antifreeze hydrometer. Write it down, and leave a note for the next guy. Ya never know. It might be you (:-o)