I have been reading the wall for several years, just bought a house in S. Vermont with steam heat. I have a one pipe steam system with two mains each approx 45 feet long, 2.5 inch o.d. pipe. They currently have Dole #4 main vents at the end of the mains. One of these main vents is not venting, the other works. What size vent do I replace the non-working vent with? Is the #4 appropriate for the size main? My other question involves venting radiators, in rooms that overheat I have adjusted the Dole adjustable vents to lower venting settings and this is causing some whistling. Is this normal?
Thanks Chris

Comments

  • Chris Jones_3
    Chris Jones_3 Member Posts: 12
    Steam Main Venting

    I have been reading the wall for several years, just bought a house in S. Vermont with steam heat. I have a one pipe steam system with two mains each approx 45 feet long, 2.5 inch o.d. pipe. They currently have Dole #4 main vents at the end of the mains. One of these main vents is not venting, the other works. What size vent do I replace the non-working vent with? Is the #4 appropriate for the size main? My other question involves venting radiators, in rooms that overheat I have adjusted the Dole adjustable vents to lower venting settings and this is causing some whistling. Is this normal?
    Thanks Chris
  • Both your mains

    should be vented with a Gorton #2. This is a much bigger vent than the Dole #4, which is positively Lilliputian.

    Your overheating rooms are the ones closer to the boiler, right? Once the Gortons are installed, you shouldn't have this problem.